Default Re: HSF-3 stopped working? How do you link the FAV & SYS to test system?

First of all, we need to know why the fuse was blown. It is a 15A fuse, more than adequate for the pump.

Few questions:
1. Where is the pump located?
2. The day the fuse blown, was it very cold, possibly frozen pump?

If you take the peg (jumper link) off the FAV and put it on the SYS, the pump will fire up but it won't get pass the FAV.

In order to have the system manually activated, you must leave the FAV peg on and use the spare "PRK" peg for the "SYS" test.